I am the original poster. Here are some details.

04C190P
House batteries; 3 lifeline group 31 GPL-31XT 125AH AGM
Coach battery “maintenance free”
Nations 240A 8327-240HP with international regulator
2/0 cable separator to house 125A? Breaker
BlueSea 7622 automatic separator
3 Renogy 100W solar panels
Trimetric monitor and solar controller
Trimetric settings from Bogart:
P1 - 14.3 V
P2 - 0.6%
P3 - 370 Ah
P7 - L3
P8 - set it 0.3 V higher than P15, but lower than the highest voltage your system will tolerate
P10 - 94%
P14 - 2.0 hrs
P15 - 15.3 V
P16 - 13.3 V
P20 - 7%
P21 - 0.5%
P22 - Off

Please let me know if I left anything out. Thanks! Steve
__________________
- Steve
'Blue' 2004 Chevy Roadtrek 190 Popular
rauscs is offline   Reply With Quote
Old 07-08-2023, 09:51 AM   #22
Platinum Member
 
Join Date: Aug 2010
Location: Minnesota
Posts: 11,526
Default

Quote:
Originally Posted by rauscs View Post
I am the original poster. Here are some details.

04C190P
House batteries; 3 lifeline group 31 GPL-31XT 125AH AGM
Coach battery “maintenance free”
Nations 240A 8327-240HP with international regulator
2/0 cable separator to house 125A? Breaker
BlueSea 7622 automatic separator
3 Renogy 100W solar panels
Trimetric monitor and solar controller
Trimetric settings from Bogart:
P1 - 14.3 V
P2 - 0.6%
P3 - 370 Ah
P7 - L3
P8 - set it 0.3 V higher than P15, but lower than the highest voltage your system will tolerate
P10 - 94%
P14 - 2.0 hrs
P15 - 15.3 V
P16 - 13.3 V
P20 - 7%
P21 - 0.5%
P22 - Off

Please let me know if I left anything out. Thanks! Steve

First you need to determine if you are really ever getting 100% full and triggering the auto reset of AH counter and SOC readings in the Trimetric,


Do you get to the .5% amps during your charging so that the Trimetric resets? I am suspicious that you are not getting that reset so the Trimetric may have gotten very far out of calibration.


I doesn't appear that the Trimetric lights a "fully charged" indicator so you would need to pay attention to SOC or AH counter to see if it resets to zero. For a quick check, I would check the resting for a couple of hours battery voltage with no loads or charging, voltage. Depending on the age and condition of the batteries you should see 12.8 to as high as 13.1v on them.


Once you have the meter issue confirmed or straightened out, check the charging voltage at the batteries from the Trimetric during your long drives. I think you meant that the alternator has an "internal" regulator and those have their own ideas of charge control so the voltage could be anywhere from 13.5-14.7 depending on the regulator. To get good acceptance and charging amps you need to be in the 14.3v range for the full time it takes to get to the .5%C amps.


If you are counting on the solar to finish off the charge to full, your settings likely won't be able to do that, it appears, because the maximum absorption time is set to only 2 hours and that timer will also count the time that the alternator is holding the voltage at absorption. Lifelines at 50% SOC are going to take something like 8 hours at absorption to get to the .5%C amps of charging. This time is the biggest issue with AGM batteries as most charging equipment doesn't charge that long. Many/most users of battery monitors that realize that they aren't getting full can't do anything about it with the equipment they have so they wind up changing the .5% to a much higher value so they can get the resets of the Trimetric to keep the readings of amp hours and SOC accurate. They are really just redefining what "full" is for them to a lower value than the rated capacity of their batteries.


Your low current to the batteries may just be because the batteries have more charge in them than the monitor is showing you because of no resets, and if they are at 70% instead of 55% you would already be into the current tapering phase of the AGM charge profile.


Our GC2 Lifelines would accept over .6C when at 50% discharge so I would expect you could see as much as 180 amps if the alternator could deliver that much and hold voltage.
booster is offline   Reply With Quote
Old 07-08-2023, 12:39 PM   #23
Platinum Member
 
Join Date: Oct 2022
Location: Red-Neck Riveria - (Fort Walton Beach, FL)
Posts: 136
Default

You have not mentioned the age of your house battery bank.
You began this thread 2 years back.
Were they new then - or are they now aging out?
That could be a factor - not only for charging, but your plan.

Just a thought from the peanut gallery.
phantomjock is offline   Reply With Quote
Old 07-08-2023, 04:18 PM   #24
Platinum Member
 
Join Date: Jan 2016
Location: California
Posts: 108
Default

Thanks booster for the usual concise and thoughtful post.

On a trip now, but should be home in a couple weeks. I’ll get the readings you suggested then. My solar stopped charging at the beginning of the trip (goood timing).

When the solar was working before the trip, batteries would usually be high 90’s in the morning, and top out to 100%.

Batteries are 4 years old.

Steve
__________________
- Steve
'Blue' 2004 Chevy Roadtrek 190 Popular
rauscs is offline   Reply With Quote
Old 07-12-2023, 03:00 AM   #25
Platinum Member
 
Join Date: Jan 2016
Location: California
Posts: 108
Default

Hi booster - can you suggest any changes to my trimetric settings that may help me reach the 100% SOC and reset the counters while driving?
Steve
__________________
- Steve
'Blue' 2004 Chevy Roadtrek 190 Popular
rauscs is offline   Reply With Quote
Old 07-12-2023, 10:24 AM   #26
Platinum Member
 
Join Date: Aug 2010
Location: Minnesota
Posts: 11,526
Default

Quote:
Originally Posted by rauscs View Post
Hi booster - can you suggest any changes to my trimetric settings that may help me reach the 100% SOC and reset the counters while driving?
Steve

The Trimetric meter can't do anything to get you to 100% full, but it can tell you if you are there, or not. The solar controller part can. I would guess that very few actually get to 100% on a regular basis with lead acid batteries because few chargers can get them there. Driving is a way to help get there though, if you drive long enough and the alternator regulator matches the profile you need. Solar can do the final top off.

The settings for the Trimetric that would indicate full Lifeline batteries are pretty simple

P1 setpoint voltage would be absorption voltage that Lifeline wants at 14.1-14.3v or so.

P2 is the amount of amps going to the batteries that you need to get below while at absorption voltage. Lifeline wants .5% of you rated 20hr capacity of 375ah. 250X.005=1.875 amps which is a tiny amount. New Lifelines will be able to get there or lower, but older ones may not even get there. Ours are 8 years old and still get to .5% and lower.

P3 is your 20 rated capacity of 375ah

P12 is the automatic reset to 100% when the above conditions are met when charging.

The solar controller settings are tough sometimes because of the hugely varying output you get from solar. The Trimetric is better than many in that it controls the absorption stage off the meter and will stay in absorption until the above conditions are met. The downside of this is that it might get "stuck" in absorption for long periods of time is the sun is not good enough to produce enough power to hold the absorption voltage. In itself that isn't all that bad, but if the batteries are full and it gets stuck just below absorption you can get a minor overcharge that way.

I will need to go and get a look at the SC2030 controller instructions to see how they do some things like determine when to go back into bulk charging and what they are doing with what the call the "finish charge", and then see how those settings set. That might take a day or two to get to.

Basic solar settings generically would absorption at 14.3v, 10 hours max absorption time, .5%C amps for float transition, 3-5 minutes hold time at absorption before float once conditions met, float at 13.1v, rebulk at 12.6v.


On edit:


P14 sets the max absorption time. I would put it at 10-12hr range


P15 sets max voltage during finish charge, which you will probably set to off, so set this the same as absorption voltage


P16 Float voltage 13.1v


P20 Percent overcharge before float. You will control by amps so you can set this to zero so it will go to float quickly if sun comes up on full batteries.


P21 this it the percent of capacity in amps to use on finish charge, which I don't think you should use. The instructions say you can set % or off so set to off.


I didn't see anything about a setting for rebulk, so can't do that it appears.
booster is offline   Reply With Quote
Old 07-12-2023, 04:52 PM   #27
Platinum Member
 
Join Date: Jan 2016
Location: California
Posts: 108
Default

Thanks! I need to get my solar working again, and will let you know how things go after that. -Steve
__________________
- Steve
'Blue' 2004 Chevy Roadtrek 190 Popular
rauscs is offline   Reply With Quote
Old 07-26-2023, 12:46 AM   #28
Platinum Member
 
Join Date: Jan 2016
Location: California
Posts: 108
Default

Please see my responses in RED below:


Quote:
Originally Posted by booster View Post
First you need to determine if you are really ever getting 100% full and triggering the auto reset of AH counter and SOC readings in the Trimetric,


Do you get to the .5% amps during your charging so that the Trimetric resets? I am suspicious that you are not getting that reset so the Trimetric may have gotten very far out of calibration.


I doesn't appear that the Trimetric lights a "fully charged" indicator so you would need to pay attention to SOC or AH counter to see if it resets to zero. For a quick check, I would check the resting for a couple of hours battery voltage with no loads or charging, voltage. Depending on the age and condition of the batteries you should see 12.8 to as high as 13.1v on them.


I did this "resting" voltage test and it came out at 13.1V.

I did go through the calibration, and am now confident that the charge% is correct on the TM. Currently at 66% charge, with AH counter at -162 of the 370 total, which calculates out to be correct. At one point after calibration it did show 100%, with AH of zero, so it got to 100% on the alternator during a long drive

I've done a couple tests of what the alternator is producing:
1) House 12.6V, Chassis 14.5V, Charge 57%, 85 Total Amps from alternator
2) House 14.3V, Chassis 14.5V, Charge 67%, 48 Total Amps from alternator

What can I do to figure this out / improve performance?

Thanks - Steve





Once you have the meter issue confirmed or straightened out, check the charging voltage at the batteries from the Trimetric during your long drives. I think you meant that the alternator has an "internal" regulator and those have their own ideas of charge control so the voltage could be anywhere from 13.5-14.7 depending on the regulator. To get good acceptance and charging amps you need to be in the 14.3v range for the full time it takes to get to the .5%C amps.


If you are counting on the solar to finish off the charge to full, your settings likely won't be able to do that, it appears, because the maximum absorption time is set to only 2 hours and that timer will also count the time that the alternator is holding the voltage at absorption. Lifelines at 50% SOC are going to take something like 8 hours at absorption to get to the .5%C amps of charging. This time is the biggest issue with AGM batteries as most charging equipment doesn't charge that long. Many/most users of battery monitors that realize that they aren't getting full can't do anything about it with the equipment they have so they wind up changing the .5% to a much higher value so they can get the resets of the Trimetric to keep the readings of amp hours and SOC accurate. They are really just redefining what "full" is for them to a lower value than the rated capacity of their batteries.


Your low current to the batteries may just be because the batteries have more charge in them than the monitor is showing you because of no resets, and if they are at 70% instead of 55% you would already be into the current tapering phase of the AGM charge profile.


Our GC2 Lifelines would accept over .6C when at 50% discharge so I would expect you could see as much as 180 amps if the alternator could deliver that much and hold voltage.
__________________
- Steve
'Blue' 2004 Chevy Roadtrek 190 Popular
rauscs is offline   Reply With Quote
Old 07-26-2023, 01:07 AM   #29
Platinum Member
 
Join Date: Aug 2010
Location: Minnesota
Posts: 11,526
Default

You have a big voltage drop at 85amps that is likely limiting the charge rate a lot. The fact that the chassis battery is at 14.5v it would appear that you have some big resistance in the wiring to the coach batteries.


I think you need to check all you wire sizes in those lines, connections, breakers, fuses, etc to see where the voltage drop is coming. Just check the voltage at every connection point and list them in order of location front to rear, and it should give a good indication of what is going on.
booster is offline   Reply With Quote
Old 07-27-2023, 05:15 PM   #30
Platinum Member
 
Join Date: Jan 2016
Location: California
Posts: 108
Default

In the previous example I gave with the large difference in voltages, I must have taken the sample too soon after starting the engine. Apologies.

Measuring the voltage at the battery vs at the breaker in the electrical compartment, with the breaker off, so no house battery involvement - I get a drop of 0.2 volts.

When all is connected and the car is running, the largest difference between the chassis and house voltages (given a minute to settle) that I see is .3V.

Over the last couple days, after giving things a couple minutes to settle:
1) House 14.1V, Chassis 14.3V, Charge 60%, 130 Total Amps from alternator
2) House 13.9V, Chassis 14.1V, Charge 63%, 67 Total Amps from alternator

After 15 minutes idling, alternator temp 180degrees
3) House 14.0V, Chassis 14.2V, Charge 55%, 78 Total Amps from alternator

Really appreciate your help!
Steve
__________________
- Steve
'Blue' 2004 Chevy Roadtrek 190 Popular
rauscs is offline   Reply With Quote
Old 09-17-2023, 04:52 PM   #31
Platinum Member
 
Join Date: Jan 2016
Location: California
Posts: 108
Default

Any more feedback? I've been trying to get some suggestions from Nations, but am having trouble getting answers.

Any and all input is appreciated.
__________________
- Steve
'Blue' 2004 Chevy Roadtrek 190 Popular
rauscs is offline   Reply With Quote
Old 09-18-2023, 12:41 AM   #32
Platinum Member
 
Join Date: Oct 2022
Location: Red-Neck Riveria - (Fort Walton Beach, FL)
Posts: 136
Default

Quote:
Originally Posted by rauscs View Post
Any more feedback? I've been trying to get some suggestions from Nations, but am having trouble getting answers.

Any and all input is appreciated.
They are not the only game in town...
It might pay to shop around. At least make some contacts.

Best of luck.

Cheers - Jim
phantomjock is offline   Reply With Quote
Old 09-18-2023, 01:18 AM   #33
Platinum Member
 
Join Date: Jan 2016
Location: California
Posts: 108
Default

Hey Jim - true, they aren't the only folks around, but since I bought the HO alternator from them, I'm looking to them first. We'll see how it goes!
__________________
- Steve
'Blue' 2004 Chevy Roadtrek 190 Popular
rauscs is offline   Reply With Quote
Old 09-18-2023, 11:17 AM   #34
Platinum Member
 
Join Date: Aug 2010
Location: Minnesota
Posts: 11,526
Default

Quote:
Originally Posted by rauscs View Post
Hey Jim - true, they aren't the only folks around, but since I bought the HO alternator from them, I'm looking to them first. We'll see how it goes!

How big is the alternator you bought?


Found it, you had 240 amps in the first post.


The internal regulator may be giving you some issues if it maxes at 14.3v but really shouldn't do that. If it runs at 14.3 and can hold that you only see 14 at the coach batteries unless they are high SOC. A higher setting on the absorption volt to around 1406v would give better results by some amount, but not much if in high SOC, only at lower SOC and early in absorption. I think the "normal" Chevy regulators are around 14.3v for later vehicles and about 13.9v for the older ones and finding higher voltage in an internal may be hard to do without it being a fixed voltage one. You will probably also find the internal regulator will take it to float way before the batteries are fully charge. Every internal one I have watched did that.


Seeing what you get at the start of charging at 175ah down will tell a lot about it all, I think, including how hot the alternator will get if the amps go up a lot.
booster is offline   Reply With Quote
Old Today, 03:24 AM   #35
Silver Member
 
Join Date: Sep 2022
Location: va
Posts: 67
Default

the 13.9v Booster referenced wasn't that the limp mode voltage? and shouldn't the nations alternator charge at 14.8? I do see they mention "- Universal regulator circuit adapts to internal or external sensing as well as PCM or ignition excitation with lamp control". That seems highly unlikely to do PCM or excitation voltage with the same circuit?

RAUSCS - - how and where do you have the alternator "control" wires hooked up? 4 pin? 2 pin? or 1 wire? on nations site it loks like a 4 pin?

EDIT: have you checked all the connections re-tight, and with a non-contact thermometer to see if any of the connections are hot?
__________________
2007 TurdWrek 190 popular
Todd
tlillard23 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Powered by vBadvanced CMPS v3.2.3

All times are GMT. The time now is 10:13 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2023, vBulletin Solutions, Inc.