I typed lithium and rule for the title. It's more like lifep04 and guideline but that seemed boring!
How do you know if your lifep04 batteries are at or near 80% discharged?
The answer seems to be that you don't know, can't know and won't know unless you monitor state of charge (SOC).
These posts prompted me to do some Googling.
http://www.classbforum.com/forums/f5/hymer-aktiv-5333-49.html#post49426
http://www.classbforum.com/forums/f5/hymer-aktiv-5333-50.html#post49469
A coulomb counter "battery fuel gauge" type device would seem to ideal for triggering lifep04 recharging. (I think that's how Advanced RV does it in their RV's)
Take a 400ah battery bank, set the recharge request at 80% DOD (320 net Ah out). Has to be net of other charging inputs. As soon as the net total ah out exceeds 320 then the unit triggers the engine or other type generator to start. You could have unlimited trigger points such as 50% SOC or 70% SOC - let the end user choose.
You can find several charts showing lifep04 capacity mostly depleted at much higher than expected voltages.
Here's one from TI: ( http://www.ti.com/lit/an/slyt402/slyt402.pdf )

Looks like approx 90% of the capacity of that battery is gone but at 12.72V no load.
Here's one from GWL Power: ( lithium & solar power LiFePO4, The voltage levels and the capacity of LFP cells... )

86% of the capacity used up but still 12.64V with 0.4C load. (40ah load on a 100ah battery)
This graph shows that at a 1.5C rate of discharge a dramatic fall off (think cliff!) starts at or before 12.2V (lithium & solar power LiFePO4, Restoring a partly discharged cell A customer... )

It would appear that, if triggering a recharge based on voltage, then you'd have to know both the load (rate of discharge) and the capacity of the battery bank and set the voltage trigger point accordingly as it will vary quite a bit as shown above. I don't see a one size fits all type solution with a voltage trigger but it does appear that a SOC based recharge trigger would work in all of the situations shown above.
How do you know if your lifep04 batteries are at or near 80% discharged?
The answer seems to be that you don't know, can't know and won't know unless you monitor state of charge (SOC).
These posts prompted me to do some Googling.
http://www.classbforum.com/forums/f5/hymer-aktiv-5333-49.html#post49426
http://www.classbforum.com/forums/f5/hymer-aktiv-5333-50.html#post49469
A coulomb counter "battery fuel gauge" type device would seem to ideal for triggering lifep04 recharging. (I think that's how Advanced RV does it in their RV's)
Take a 400ah battery bank, set the recharge request at 80% DOD (320 net Ah out). Has to be net of other charging inputs. As soon as the net total ah out exceeds 320 then the unit triggers the engine or other type generator to start. You could have unlimited trigger points such as 50% SOC or 70% SOC - let the end user choose.
You can find several charts showing lifep04 capacity mostly depleted at much higher than expected voltages.
Here's one from TI: ( http://www.ti.com/lit/an/slyt402/slyt402.pdf )

Looks like approx 90% of the capacity of that battery is gone but at 12.72V no load.
Here's one from GWL Power: ( lithium & solar power LiFePO4, The voltage levels and the capacity of LFP cells... )

86% of the capacity used up but still 12.64V with 0.4C load. (40ah load on a 100ah battery)
This graph shows that at a 1.5C rate of discharge a dramatic fall off (think cliff!) starts at or before 12.2V (lithium & solar power LiFePO4, Restoring a partly discharged cell A customer... )

It would appear that, if triggering a recharge based on voltage, then you'd have to know both the load (rate of discharge) and the capacity of the battery bank and set the voltage trigger point accordingly as it will vary quite a bit as shown above. I don't see a one size fits all type solution with a voltage trigger but it does appear that a SOC based recharge trigger would work in all of the situations shown above.