There is a lot more information there, and here is the problem description as you stated there. I just read it.
Problem Description
- 2.4 kw Generator operates A/C fan (which continues to run), but the compressor stops intermittently within 1-4 minutes (A/C load 14 amps/fan 3 amps alone, continuous 114 volts)
- A/C operates from generator properly when wired directly from the generator (eliminating transfer switch, inverter, breakers, etc.)
- A/C works great on 30 Amp Shore Power going through total system transfer switch, inverter, etc.
- A/C operates great on inverter.
- Microwave operates fine through the normal system while operating on the generator with a similar 13 amp load
I think that this is probably lending support to the bad transfer switch theory
The fact that the genny runs the AC fine with transfer switch is bypassed in the key, IMO.
What I think may be happening is confusing but does make sense, at least the me
The transfer switch is shore power first priority and if it fails that is where it will always be. Everything runs great when on shore power on your description, including the AC.
When on generator, the microwave works but the AC only kinda works. The fan runs OK, but keeps cycling with compressor on. That may mean it just can't handle reduced amps from some source.
The short recycling to on time is typical of an AC unit if it shuts down for some reason as it is a recycle timer to prevent tying to start against built up back pressure in the compressor.
The microwave runs OK on generator, but is it running on the generator or inverter? That is going to be the key to all of this. My guess it is running of the inverter and it keeps running because it doesn't have the huge surge of a compressor starting like the AC. The AC is trying to run on inverter but it can't supply enough power to restart the compressor, maybe because of low batteries, maybe AC has a bad start capacitor, or some other reason. Most likely low batteries.
You have gotten to transfer switch, it appears, so time to get a clamp on ammeter onto the wire into it from the genny and then out from the transfer switch. My guess again would be there won't be any.
The confirmation test you might want to run would be to try the microwave with neither shore or generator power. If it runs OK you know it is on inverter as it is the only power. Then try the AC unit the same way and see if the fan runs and compressor won't run and you would have your answer. Change the transfer switch out if it behaves that way.
With a system as you describe there is probably an automatic transfer switch at the AC input point from shore and generator wired shore priority.
To be able to use an inverter with the single automatic transfer switch, you need a second automatic transfer switch and in the Multiplus literature it says that is inside the Multiplus.
With this system, the inverter will not but out power unless there is no AC power to the Multiplus so if the first transfer switch fails to switch to generator throughput, the Mulitplus turns on the inverter.
It should be pretty easy to look for AC power at the input to the Multiplus when on shore and generator to see what is really going on.