07-24-2023, 09:28 PM
Electrical System integration advice…
Hey y’all! I own a 1991 Dodge B250 Roadtrek 190 versatile. I’m preparing to install solar, a battery, and an inverter into the existing electrical system. I’m very inexperienced, and this is my first project involving electrical work. I’ve been cramming as much info as possible in preparation for the install, and I’ve even illustrated a (very crude) diagram laying out the components and connections(attached file). I’m not certain if my setup is viable as I have designed it, and I’m looking for the more experienced folks on this forum to basically tear it apart and let me know what’s wrong with my plan so that I can do this correctly the first time. There are some connections in the diagram that I assume are possible, but I suspect there may be quite a bit that I have yet to account for, hence this “call for help”. Any and all advice/info is greatly appreciated, as well as any online resources that y'all think might be useful for this project of mine.
07-24-2023, 09:38 PM
You must be going to use a solar controller with the second input for the alternator?
The AC output from the inverter would normally go to an automatic transfer switch before the breaker panel so it could select which AC to use, shore power or inverter.
07-25-2023, 12:00 AM
UPDATE: learned that I can disconnect the battery charger part of the power converter, eliminating the death loop workaround. Here is my new simplified plan. Feedback is appreciated!
07-25-2023, 12:01 AM
Also, the shore power connection will be plugged into the the inverter, eliminating the need for an AC input switch.
07-25-2023, 12:17 AM
I think you need to read up on the rules for neutral/ground bonding requirements and locations. They pretty much eliminate having the shore and inverter output tied directly together.
Your inverter should have automatic bonding when it is on, but may be permanently bonded so be sure to find out. Shore power is required to be bonded all the time. Both should not happen at the same time.
Your grounds are to the chassis and having things tied together can give you AC voltage on the body of the van which can be very harzardous.
Best to put in the auto transfer switch and be done with it so you have isolated neutrals for both sides.
07-25-2023, 07:45 AM
Thank you for your responses! After looking Into it, the inverter is internally bonded, if that means that the neutral and ground are connected internally. Is a ground wire from the negative battery terminal to the chassis the only ground connection I’d need to worry about?
07-25-2023, 11:17 AM
If the inverter is internally bonded permanently which it sounds like and not auto bonded at use, that inverter cannot be connected directly to the same connections as shore power as you would have two neutral ground bonds in different places and one and only one are required for safety reasons. Keeping the shore power and inverter separated all the time is what the automatic transfer switch does as it switches both the power and ground leads on and and off for each source.
07-25-2023, 09:07 PM
I'm having trouble finding info on if the Renogy 2000W Pure Sine Wave Inverter that I'm using is permanent or auto bonded. Is there any jerry riggery that can be done to eliminate one of the two neutral ground bonds if needed? I'm trying to keep this project simple, and I know the size of my inverter/battery/solar will be sufficient for my needs, I think I just need to take a good look at the existing system, and connections, to see exactly where these new additions will need to fit. Also, could you elaborate some on why I shouldn't simply plug my shore power connection into my inverter, and power the van solely through the inverter?
07-25-2023, 09:25 PM
If your inverter is really and inverter/charger, you can put AC into it. If it is just an inverter, power only comes out of it. If it has an outlet on it you would have to rig a cheater cord with a plug on both ends and that is considered a recipe for disaster and it does nothing to fix the bonding issues.
If you want the system to be simple, you should just ditch the old Magnetek converter and buy an inverter/ charger that has a built in transfer switch and autobonding They are getting to be more common all the time now as everybody and the manufacturers are catching on to convenience and no worry.
But, I don't understand the resistance to using an auto transfer switch on what you have. They are only 6 wires in (the shore power three and the inverter output three) and 3 wires out to all the stuff you want to power in the van from either source. Very easy to do and safer besides.
07-25-2023, 09:38 PM
So I think if I went with the auto switch like you mentioned, id have to cut the shore power cord, attach the converter side of the cord to the switch output, and the inverter output + the other side of the shore power cord into the switch input? and that would eliminate the double neutral grounding issue with the shore power cord directly hardwired to the inverter?
07-25-2023, 09:52 PM
It should do all of that. As long as you don't have a generator in the van, which hasn't been mentioned as it would be another source.
07-26-2023, 12:17 AM
I believe I’ve updated the diagram to reflect the changes that you mentioned. I’m sure there’s more to be done in that regard but do I look like I’m on the right track now?
07-26-2023, 12:27 AM
You have one other advantage now with the transfer switch in that the converter can be connected full time now.
Just wired it into the shore power line before the transfer switch.
07-26-2023, 01:27 PM
- I think you need to fuse the chassis battery lead.
- I'm not understanding the 200A fuse on the 120V side of the inverter. Seems like the wrong value, and perhaps isn't necessary at all.
- Best to have a disconnect on the solar side of the MPTT. Makes maintenance simpler.
07-26-2023, 01:44 PM
Yep, I agree, no fuse at all normally needed on the 110vac side as that is usually built in to the inverter and 2000 watts will not overload correctly sized wiring that includes surge anyway.
Probably would be good to fuse the chassis battery line, unless current limiting is built into the controller, which it might be.
It would be nice to see what all the components will be by brand and model so we could get a look at the voltages/profiles involved as it will be lithium and holding at high voltages isn't a great thing to do and if the voltages are badly mismatched some sources may not contribute very well. Same with the lithium battery as how the BMS handles things will be important in that system as it doesn't appear that there will be no independent charge controls in place so all control will be with the BMS itself. Personally, I don't care for having the BMS cycling all the time on what originally were probably designed to be safety protections, but apparently lots of manufacturers think it is OK now?
07-27-2023, 01:54 AM
This is my current iteration of the diagram. I did read your reply about the 200a on the 120v side, makes sense, I’ll take that one out. Can you explain what you mean by fusing the chassis?
07-27-2023, 04:24 PM
You are closing in on it. You do need a fuse in the solar output to the battery line and also on both ends of the cable from the alternator to the battery that is sized properly to what the alternator is capable of.
Be aware that the lithium battery is likely to absorb more amps than the alternator, and maybe the wiring, can handle so some kind of limiting will probably be needed. Most people use a b to b charger for that purpose. I would not even start the engine with the lithium battery in place until you get that worked out our have fusing in place to protect the wiring and alternator and you will probably blow them quickly. For 200 amps you are going to need to have a big alternator and big cable, but most limit to 40 or 80 amps with a b to b and have about a 6ga cable that can handle 80 amps. Many alternators can spare that much without overheating.
07-27-2023, 05:23 PM
For any current source that can produce enough current to overload the wire attached to that source, you fuse as close to the current source as possible. The chassis and lithium batteries are sources which can produce enough amps to smoke wires, therefore wires from those batteries must be fused close to those batteries.
You also might have to fuse any place where you step down in wire size. For example, if all sources feeding a bus bar are fused with 200A fuses, but you are taking power off that bus with 10ga wire, the source side of that 10ga wire should be fused to protect that wire against a possible 200A surge if it's accidently shorted out.
AFAIK - If you have at least 10ga. wire from the panels, your solar panels might not need to be fused. The max current from two 200W 12v panels will be around 25 amps, which can be carried by 10ga. wire, thus a fuse might be optional.
See: https://explorist.life/how-to-fuse-a...y-not-need-to/
In an earlier version, you had a combined MPPT/DC-DC controller/charger. That was a much better idea, as it eliminates the need for a combiner.
I would not cut into the wire between the alternator and battery. In most cases it will be better to take power from the battery terminal directly, properly fused of course.
07-27-2023, 05:51 PM
The other reason you probably want a battery to battery charger between the house and chassis systems is the voltage from the alternator may not be enough to fully charge your lithium batteries. I had mine connected through a battery isolator/disconnect, and the house batteries could never be fully charged by the engine
07-27-2023, 06:48 PM
Systems Integration
I believe if you are combining a house Lithium battery bank with a starting battery that is lead acid/sealed maintenance battery; the isolator is the wrong device. The reasonable choice is a battery to battery (DC2DC) charger.
The isolator still has a place with a house bank that is AGM or Gel and a "standard" starting battery and a "smart regulator."
Cheers - Jim