Quote:
Originally Posted by RT-NY
Yes, the manual does does say that, but it says to run it under load:
"To prevent harmful moisture accumulation and fuel deposits, run the genset at 50 percent capacity (1,400 watts) for two hours every four weeks."
|
When you are running at very low loads, the engine will be running at least somewhat on the idle circuit fuel delivery passages, which are very small and the ones that are most likely to gum up from stale gas/lack of use. Symptoms would be the same as those same issues at no load such as surging and backfiring.
If it runs well at idle and responds to loads going on without dying or backfiring, it will probably also run well at low loads.
If it does surge, etc you could run some seafoam through it to clean the passages and possibly turn the altitude knob to a lower altitude to see if that helps.